1 ton of air-con is defined as 3577 watts

Therefore 20 tons is 71.5 kW. On a 240 v 3-ph system the current for that is 100 amps, assuming a 240 v line-to-neutral voltage, equivalent to a phase-to-phase voltage of 415 v.

User Avatar

Wiki User

12y ago

What else can I help you with?

Related Questions

How many amperes for 3 phase 220v 5 tonner?

50 Amps Single Phase 20 Amps Three Phase


How many amps 50 hp 240 3 phase?

106 amps


How many amps per phase will you get on 7kw?

9


How many amps on 3 phase 225 amp panelboard each phase?

In a three-phase 225 amp panelboard, each phase will carry 225 amps. This means that the total current flowing through the panelboard is distributed evenly across the three phases, allowing for a maximum of 225 amps on each phase at a time.


How many amps will a 240 volt single phase 15 kva generator supply?

62.5 amps


How many amps in 17000 watts?

At 240v single phase it's 70.8 amps. If it runs on 2 wires plus ground, take the voltage rating of the equipment and divide that into the watts to get amps. At 480v 3 phase it's 25.8 amps. At 208v 3 phase it's 47.2 amps. <<>> There are zero amps in 14 kW. A voltage needs to be stated. I = W/E, Amps = Watts/Volts.


How many amps in 6 kw?

UK Mains is 230V therefore 6 KW is 6000/230 = 26 Amps. 3 phase is slightly different....... 6000/400V = 15 Amps/root 3 = 8.67 Amps per phase.


How many amps are available in a three phase 225 amp panel?

In a three phase 225 amp panel, there would be a total of 225 amps available for each phase, making it a total of 675 amps for all three phases combined. This means that you could have up to 225 amps of current flowing through each phase simultaneously.


How many amps does a 2000 watt heater draw at 240 volts on each line?

For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.


How many amp in kw?

UK Mains is 230V therefore 6 KW is 6000/230 = 26 Amps. 3 phase is slightly different....... 6000/400V = 15 Amps/root 3 = 8.67 Amps per phase.


How many amps is 6kW 240 volt single phase?

The equation that you are looking for is Amps = Watts/Volts. There are 6000 watts in 6kW.


How many amps will a 50KVA 3phase bank carry on 277 - 480 volts?

50 kVA is 16.667 kVA per phase and you divide that by the phase voltage. Current = 16667 / 277 = 60 Amps