answersLogoWhite

0


Best Answer

To answer this question the voltage of the immersion heater is needed. I = W/E.

User Avatar

Wiki User

2011-07-21 08:06:50
This answer is:
User Avatar
Study guides

Add your answer:

Earn +20 pts
Q: How many amps breaker you need for a 5000 watts immersion heater?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How much current would a 5-kW heater draw with 230 volts?

The formula you are looking for is I = W/E, Amps = Watts/Volts. Amps = 5000/230 =21.7 amps. The wire size to run this heater would be a #10 copper conductor. The supply breaker would be a two pole 30 amp breaker.


How many watts is in 500kva?

5000 watts


Can you run a 277volt heater on 220 volts?

Yes, you can but the wattage output rating of the heater will not be reached due to the lower applied voltage. For example if the heater is 5000 watts at 277 volts, the current is I = W/E 5000/277 = 18 amps. The resistance of the heater is R = W/I (squared) = 5000/18 x 18 (324) = 15.43 ohms. Applying 220 volts on the same heater whose resistance is 15.43 ohms results in this new heater wattage rating. W = E (squared)/R = 220 x 220 (48400)/15.43 = 3137 watts. W = watts, I = amperage, R = resistance in ohms and E = voltage.


Can you run a 277 single phase heater on a 220 single phase?

Yes, you can but the wattage output rating of the heater will not be reached due to the lower applied voltage. For example if the heater is 5000 watts at 277 volts, the current is I = W/E 5000/277 = 18 amps. The resistance of the heater is R = W/I (squared) = 5000/18 x 18 (324) = 15.43 ohms. Applying 220 volts on the same heater whose resistance is 15.43 ohms results in this new heater wattage rating. W = E (squared)/R = 220 x 220 (48400)/15.43 = 3137 watts. W = watts, I = amperage, R = resistance in ohms and E = voltage.


What does high or low voltage do to the capacity of an electric heater?

Yes, voltage effects the output of electric heaters. The wattage output rating of the heater will not be reached due to the lower applied voltage. For example if the heater is 5000 watts at 277 volts, the current is I = W/E 5000/277 = 18 amps. The resistance of the heater is R = W/I (squared) = 5000/18 x 18 (324) = 15.43 ohms. Applying 220 volts on the same heater whose resistance is 15.43 ohms results in this new heater wattage rating. W = E (squared)/R = 220 x 220 (48400)/15.43 = 3137 watts. W = watts, I = amperage, R = resistance in ohms and E = voltage.


How many amps does 5000 watts require?

Ohm's Law - Volts times Amps = Watts. For 5000 Watts at 120 Volts, the Amperage would be 41.667.


Who is Michael 5000 watts?

Micheal Jackson is a hip hop and r&b singer.And he made the song"5000 watts"


What size wire and breaker do you need for a 5000 watt garage heater?

Look on the heater and see what amps it is pulling. That will determine the wire size and breaker size. It must be on a dedicated circuit. 15 amps = AWG # 14 wire with 15 amp breaker 20 amps = AWG # 12 wire with 20 amp breaker 30 amps = AWG # 10 wire with 30 amp breaker 40 amps = AWG # 8 wire with 40 amp breaker


Can you connect a 208volt electric heater to 240 volts?

Yes <<>> The heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced. For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating. W = watts, I = amperage, R= resistance in ohms and E = voltage.


Can a 5000 watt generator run your furnace?

Not if the furnace exceeds 5000 watts.


Can you feed a 208 volt baseboard heater from a 240 volt circuit?

208 volt heater on 240 voltsNo, the heater will operate higher than its given specified nameplate wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced.For example if the heater is 5000 watts at 208 volts, the current is I = W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) = 5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.W = watts, I = amperage, R = resistance in ohms and E = voltage.


What happens when a 208 volt element is used in water heater on a 240 volt circuit?

208 volt heater on 240 voltsThe heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced.For example if the heater is 5000 watts at 208 volts, the current is I = W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) = 5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.W = watts, I = amperage, R = resistance in ohms and E = voltage.