1 watt RMS equals to 100PMPO , accordingly 1000watt RMS equals to 10,000 PMPO. check out LG Home Theater HB954TB for the same.
162 X 5000= 810,000
The GCF is 1.
15,000
5000 del peru
A 5-kW electric heater rated at 240 volts is equal to 5000 watts. To convert kilowatts to watts, you multiply by 1000. So, 5 kW is equivalent to 5000 watts.
Look on the heater and see what amps it is pulling. That will determine the wire size and breaker size. It must be on a dedicated circuit. 15 amps = AWG # 14 wire with 15 amp breaker 20 amps = AWG # 12 wire with 20 amp breaker 30 amps = AWG # 10 wire with 30 amp breaker 40 amps = AWG # 8 wire with 40 amp breaker
Yes, you can but the wattage output rating of the heater will not be reached due to the lower applied voltage. For example if the heater is 5000 watts at 277 volts, the current is I = W/E 5000/277 = 18 amps. The resistance of the heater is R = W/I (squared) = 5000/18 x 18 (324) = 15.43 ohms. Applying 220 volts on the same heater whose resistance is 15.43 ohms results in this new heater wattage rating. W = E (squared)/R = 220 x 220 (48400)/15.43 = 3137 watts. W = watts, I = amperage, R = resistance in ohms and E = voltage.
Yes, voltage effects the output of electric heaters. The wattage output rating of the heater will not be reached due to the lower applied voltage. For example if the heater is 5000 watts at 277 volts, the current is I = W/E 5000/277 = 18 amps. The resistance of the heater is R = W/I (squared) = 5000/18 x 18 (324) = 15.43 ohms. Applying 220 volts on the same heater whose resistance is 15.43 ohms results in this new heater wattage rating. W = E (squared)/R = 220 x 220 (48400)/15.43 = 3137 watts. W = watts, I = amperage, R = resistance in ohms and E = voltage.
The formula you are looking for is I = W/E, Amps = Watts/Volts. Amps = 5000/230 =21.7 amps. The wire size to run this heater would be a #10 copper conductor. The supply breaker would be a two pole 30 amp breaker.
No, you cannot use an existing 8 3 wire hooked to a 30amp breaker for a heater that requires 10 2 wire. The wire gauge and breaker size need to match the specific requirements of the new heater to ensure safety and proper function. You will need to upgrade the wiring to accommodate the 10 2 wire needed for the 5000-watt 240-volt heater.
Micheal Jackson is a hip hop and r&b singer.And he made the song"5000 watts"
The average size water tank is 4500 watts. The generator's supply will be large enough to operate the water tank. Larger tanks over 5000 watts will not heat correctly.
To find amps if watts and volts are known, use the formula; watts / volts = amps or 5000 / 240 = 20.83 amps
Not if the furnace exceeds 5000 watts.
5000 watts is equal to 5 kilowatts because 1 kilowatt is equal to 1000 watts. So, to convert watts to kilowatts, you simply divide the wattage by 1000.
Look for a professional styled hair dryer since they go to 5000-Watts. Commercial hair dryers tend to not exceed 2000-Watts.