answersLogoWhite

0

For single phase, KVA = (line to ground) * (phase current).

A 75kVA 480 to 208Y/120 volt transformer is a fairly common transformer. I assume this is the type of transformer you are referring to. 75k / 120 = 625 Amps.

As an FYI, the 208Y voltage is the line to line voltage, which is equal to (phase 1) - (phase 2), where the phases are separated by 120 degrees, thus (phase 1) * 1.732

For three phase, kVA = (line to line voltage) * (phase current) *(sqrt 3),

75k / 208 / 1.732 = 208 Amps.

User Avatar

Wiki User

15y ago

What else can I help you with?

Related Questions

How many amps can you get from a 500Kva transformer?

The amps you can get from a 500 kVA transformer would depend on the voltage of the transformer's output. To calculate amperage, you can use the formula: Amps = Power (kVA) / Voltage. For example, if the output voltage is 480V, you would get approximately 1041 amps (500 kVA / 480V).


Can you use a step up transformer 110220 with output of 16 kva?

Yes, but your input current is going to be high at 133 amps. The output of the transformer is not going to be 16 KVA, that is the rating of the transformer.


How many amps will a 250 kVA transformer in 220 volts secondary?

To calculate the amperage in the secondary side of a transformer, you can use the formula: Amps = kVA / (Volts x Sqrt(3)). For a 250 kVA transformer with a 220-volt secondary, the amperage will be approximately 660.4 Amps.


How much actual power does a 1KA transformer provide?

The kVA represents the power-handling capability of the transformer.So, if you were using a 1 kVA transformer at 110 volts, you could roughly estimate the maximum output to be 9 amps.


How many amps will a 37.5 KVA transformer carry?

It depends on the rated voltage of its secondary.


How do you calculate the output voltage of a transformer if kva rating is known?

You can't determine the output voltage of a transformer by knowing kva. Transformers will be marked as to input and output voltages. Some will have multiple input and output voltages. The output voltage depends on the ratio of coil turns between input and output.


How many output amps from a 75kva transformer fed with 480 ckt.?

It depends on what the output voltage is. You only specified the input voltage, not the output voltage. The equation is 75 Kva = {some} amps times {some} kilovolts. (Minus incidental losses, of course, but you still need to know output volts.)


Unanswered questions-how many amps for a 500KVA transformer.?

To determine the amps for a 500 kVA transformer, you can use the formula: Amps = kVA × 1000 / (Voltage). For example, at a standard voltage of 480V, the calculation would be 500,000 VA / 480V, which equals approximately 1041.67 amps. The specific current will vary based on the voltage level used with the transformer.


How many output amps is a 45 kva transformer?

There is not enough information provided to answer. KVA is short for "Kilo Volt Amperes". That is, thousands of Volt Amps. In order to determine how many Amperes are flowing, you must know at what voltage it is operating. Amperes = 45,000 ÷ volts Bill Slugg


How many amps on 25 kva transformer 1phase secondary 230 volts?

Take the KVA and divide it by the voltage. 25/.230 = 109 amps. The transformer can put out up to 50% more that its rated for short durations. So you could get around 150 amps out of a 25 Kva tranformer in a worst case situation.


How many output amps is a 75 KVA generator single phase?

The formula you are looking for is , A = kva x 1000/Volts.


What size ground wire for a 30 kva transformer?

The size of grounding wire is based on the amperage output of the transformer. The voltage of the transformer needs to be stated. Without this voltage a calculation can not be made. Amps = Watts/Volts = 30000/?.