answersLogoWhite

0


Best Answer

Yes it can.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can a difference of 5 milliamperes for 30 milliseconds trip a gfci?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

Will another electrical outlet that is in line with a GFCI outlet cause it to kick off?

A down stream receptacle that is connected to the upstream GFCI will be protected. If the downstream receptacle senses a fault the upstream GFCI will trip.


Does the gfci outlet beep when there's aproblem?

No, it will just trip and cut off the power.


What causes gfci receptical to trip when fan is turn on?

There is likely an internal short circuit in the fan motor.


GFCI circuitry checks for what?

Current Imbalance: GFCIs continuously monitor the current flowing in the "hot" (live) wire and compare it to the current returning in the "neutral" wire. If there is a difference of as little as 4-6 milliamperes (mA) between these currents, indicating that some current is not returning through the normal circuit path, the GFCI will trip and disconnect the power. Leakage to Ground: GFCIs are designed to detect any unintended flow of electricity to ground, which could be potentially hazardous. This can occur when there's a fault in an electrical device, damaged wiring, or when someone comes into contact with a live wire or conducts electricity to the ground. Rapid Response: GFCIs are engineered to respond quickly, typically tripping within milliseconds when they detect a ground fault. This rapid response helps prevent electric shocks and electrical fires.


Is removing a gfci dangerous?

it is not wise to remove this device it is in place for your safety it is also wise to note over time these device do false trip for no reason.Some will trip with an induction load like a fridge . have it tested .........................

Related questions

What is the trip time for a GFCI?

A GFCI (Ground Fault Circuit Interrupter) is designed to trip within milliseconds when it detects a fault, such as a ground fault or leakage current. This rapid response helps to protect against electric shock by quickly shutting off power.


How much amperage is needed to trip a 20amp GFCI outlet?

A 20 amp GFCI outlet will trip when the current exceeds 20 amps by a certain amount, typically around 5 mA to 6 mA, which is the typical trip threshold for GFCI outlets.


What is the function of GFCI?

A GFCI or Ground Fault Circuit Interrupter is designed to trip and stop the flow of electricity when there is a difference in the flow of electricity between the hot and neutral wires. Normally the difference will be near 0. If someone drops an appliance into the water this creates a situation where there is a difference and the breaker will immediately trip thus protecting people from electrocution.


What happens if you trip a GFCI repeatedly on purpose?

Every time you trip the GFCI, the power to the device plugged into it will lose its supply voltage.


How many amps does gfci trip at?

GFCI receptacles are designed to trip at around 5 milliamps (0.005 amps) of current leakage to ground. When the GFCI detects this level of imbalance, it quickly shuts off the power to prevent electric shock.


Will starting current on a motor trip a gfci breaker?

A GFCI measures difference in output to return current. A Overload breaker in your panel is what trips from too much current. many are time delay and will not trip immediately from the less than a second of start up current spike.


Will a GFCI outlet trip when the current is reduced or shut off?

A GFCI outlet will trip when it detects a ground fault, not when the current is simply reduced or shut off. The purpose of the GFCI outlet is to quickly shut off power when it senses a potential electrical hazard, such as a ground fault or leakage.


Will another electrical outlet that is in line with a GFCI outlet cause it to kick off?

A down stream receptacle that is connected to the upstream GFCI will be protected. If the downstream receptacle senses a fault the upstream GFCI will trip.


Can rodent damaged romex cause gfci to trip?

Yes, rodent damage to Romex can cause a ground fault circuit interrupter (GFCI) to trip. Rodent chewing on the wiring can expose the copper inside, leading to a ground fault. When the exposed wire contacts a grounded surface or another wire, the GFCI will trip to prevent electric shock or fire hazard.


A GFCI device in a breaker is intended to?

A GFCI device in a breaker is intended to trip the breaker open when a ground fault is sensed in the circuit that the breaker is protecting.


What happens when you plug a GFCI protected extension cord into an outlet that is GFCI protected?

When a GFCI-protected extension cord is plugged into an outlet that is also GFCI protected, it provides an additional layer of protection against electric shock. Both devices work in conjunction to quickly detect any imbalance in the electrical current and trip the circuit if necessary. This redundancy helps ensure increased safety against electrical hazards.


How do you determine if an outlet is after or before the gfci?

You can determine if an outlet is after a GFCI by pressing the "test" button on the GFCI outlet. If the GFCI trips and cuts off power to the outlet, then that outlet is downstream from the GFCI. If power is not cut off, then that outlet is upstream from the GFCI.