0


Best Answer

To answer this question, the voltage to be used on the plug must be stated. With no voltage stated the answer is no. The smallest generator to obtain 50 amps is a 6000 watt generator.

The output of a 5600 watt or 5.6 kW generator in amperage using 240 volts is 5.6 x 1000 = 5600/240 x 1 = 23 amps.

Equation to use for single phase calculations is Amps = kW x 1000/Volts x pf.


For calculation purposes use 1 as a pf consonant. Generators that are commonly used in residential environments usually have a power factor of 1.0.


Amperage for each "hot" leg to neutral is 5600/120 x 1 = 46 amps. The only trouble using 120 volts is that on this type of generator, the 120 volt circuits are connected to the duplex receptacles. These receptacles are protected at 15 amps each.


You would need to have access to the generators junction box to change the generators output leads. Even then, all you will obtain is 46 amps.

A 6000 watt or 6 kW generator at 120 volts will give you 6000/120 x 1 = 50 amps.

A 12000 or 12 kW generator at 240 volts will give you 12000/240 x 1 = 50 amps.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

9y ago

If it's a 120 v system the generator is marginally adequate. If it's 240 v, no.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Will a craftsman 5600 watts generator run a 50 amp plug?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Can you plug a power strip into a generator to run multiple items?

Yes, you can plug a power strip into a generator to run multiple items, but it's important to ensure that the overall power draw of the devices plugged into the power strip does not exceed the generator's capacity. Be mindful of the total wattage of all items connected to the power strip to avoid overloading the generator.


On output from gas generator generac mod g1000?

If you are experiencing issues with the output from your Generac G1000 gas generator, it is recommended to check for any clogs in the fuel system, clean the fuel filter, and ensure the spark plug is in good condition. Additionally, verify that the air filter is clean and check the oil level. If problems persist, it may be necessary to contact a professional technician for further assessment and repairs.


What can you power with a 3000 watt generator?

A few small things. Watts = Amps x Volts. Amps = 800/120 = 6.66 amps. Check the amperage on what you want to plug into the generator. If it is over 6 amps the generator will not handle the load.


What will a 300 watt generator run?

A generator this size will generally have 1 240 V/30-Amp receptacle and 1 or 2 20-Amp/120V receptacles. You cannot exceed the rating of these receptacles. There are very few 240 V/30 amp appliances which are less than 3000 watts. Most dryers are rated for at least 5000 watts; water heaters generally will use a minimum of 3800 watts. The best you can do is get a 240V to 120V plug converter, which will convert the 30 Amp plug to a few 120 V plugs. 120 V Microwaves will use close to 1500 watts and 12.5 amps. 120V space heaters will use about the same amount as microwaves. You also must remember that loads such as motors will need a higher starting current than a running current. Most generators have two ratings. The one which will temporarily handle a higher starting current, and the one which will handle a longer-term running current. A 3000 watt generator probably has a maximum current rating that is higher, but this is only to be used for a short time. Be certain that any loads, when starting, will not exceed the maximum starting current load of the generator.


How many watts does a satellite DVR receiver use?

A satellite DVR uses about 80 watts. This value can be found where the plug in cord meets the chassis of the recorder.

Related questions

What is the spark plug gap for a Brigs and Stratten generator?

the plug gap for generator is 0.70 mm


What is the spark plug gap for a craftsman?

.030"


What is the Spark plug gap for a craftsman 143.976600?

.030"


Can you plug in a 1650 watts into a 20 AMP plug?

Yes.


Where is the oil drain plug on a Craftsman Kohler Pro - 23hp V-Twin?

Where is oil plug


What type of spark plug for a craftsman 6.0 lawnmower?

Rj19l


How do you measure watts output of a generator?

To do it yourself you will have to be familiar with an amp meter, and ohms law, and be able to trace to main wire leads from the stator windings. I'm sure that an electric motor repair shop would do it for you cheaply. Have you closely examined all tags and labels on the unit? Take the cover off and look real good. UL requires that all manufacturers properly tag all equipment with capacities. A quick rule of thumb, take the amperage of the breaker that protects the plug on the generator. Multiply this amperage by the voltage that comes from the plug. This will give you an indication of the power in watts that this generator should be able to produce. Watts = Amps x Volts.


What model spark plug for a craftsman chainsaw?

My 16" Craftsman 36 cc chainsaw manual calls out for a Champion RCJ7Y....if that is the same size chainsaw as yours, I would go with that plug.


Can you plug a 220 well pump into a 240 generator plug in?

Not advisible.


How many watts comes out of a portable generator 120volt outlet?

This is calculated using OHM's LAW, a set of mathematical equations, where TWO facts must first be known to calculate DIRECT CURRENT (DC such as a car battery system) or THREE facts must first be known to calculate ALTERNATING CURRENT (AC as in the portable generator or a household electrical outlet.) In order to determine WATTS for a generator producing 120 volts AC we also need to know the AMPs the generator is capable of producing and its POWER FACTOR (PF). Since the question reveals just ONE of the three facts (volts) to be known, an answer cannot be calculated. The formula is WATTS = VOLTS x AMPS x PF. If the "nameplate" containing the required information is missing there is a simple way to estimate the generator's WATT capability. Run the generator, plug in a bank of light bulbs. Start with perhaps five 100 watt bulbs to equal 500 watts. Add additional 100 watt bulbs until the circuit breaker "pops" and the bulbs are turned off or the generator quits. If electricity quits with 11 light bulbs (1,100 watts), remove one light bulb and try just 10. If this works okay the generator can be estimated to produce 1,000 watts. 15 bulbs would equal 1,500 watts. Light bulbs will be the most accurate "load" on the generator for estimating wattage. You can also attempt to determine the make and model number of the generator and search the Internet for its specifications or contact the manufacturer direct. -- BF


Craftsman leaf blower Model 358.797310 What is the spark plug gap?

Spark Plug gap is .025


Where is the oil plug for the craftsman 6.5 lawnmower?

Your owner's manual should explain that.