Absolutely not!! 277 volts is developed from a 480 volt power supply employing 1 conductor and a neutral. 240 volt power comprises two hot conductors and NO neutral.
9000 BTU/hour is equivalent to 2300 watts so the heater will draw 10 amps on 230 volts.
To calculate the amp draw for a 3800-watt water heater at 240 volts, use the formula: Amps = Watts / Volts. Thus, the amp draw would be 3800 watts / 240 volts, which equals approximately 15.83 amps. Therefore, the water heater draws about 16 amps.
The formula you are looking for is I = W/E.
To calculate the amperage for a 240-volt, 1500-watt electric baseboard heater, you can use the formula: Amps = Watts / Volts. For this heater, it would be 1500 watts / 240 volts, which equals 6.25 amps. Therefore, the heater uses approximately 6.25 amps.
A 50 gallon electric water heater with 2 elements is typically connected to a 240 volt power supply. Each element is designed to run on 240 volts to efficiently heat the water in the tank.
Watts = Amps x Volts. 33 x 240/1000 = 7.9 Kw
9000 BTU/hour is equivalent to 2300 watts so the heater will draw 10 amps on 230 volts.
VOLTS x (VOLTS/OHMS) = WATTS 240 X (240/8) = 7200 Watts = 7.2KWatts
To calculate the amp draw for a 3800-watt water heater at 240 volts, use the formula: Amps = Watts / Volts. Thus, the amp draw would be 3800 watts / 240 volts, which equals approximately 15.83 amps. Therefore, the water heater draws about 16 amps.
Usually with 240 volts. Some under 1000 watts will use 120 volts.
The formula you are looking for is I = W/E.
To calculate the amperage for a 240-volt, 1500-watt electric baseboard heater, you can use the formula: Amps = Watts / Volts. For this heater, it would be 1500 watts / 240 volts, which equals 6.25 amps. Therefore, the heater uses approximately 6.25 amps.
In the USA it is either 120/208 or 120/240 depending on your local unility company
A label.
For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.
No. A water heater requires a 240 volt connection and cannot be re-wired to run on 120 volts. There isn't enough amperage in 120 volts to power the heating rods that are inside.
A 50 gallon electric water heater with 2 elements is typically connected to a 240 volt power supply. Each element is designed to run on 240 volts to efficiently heat the water in the tank.