answersLogoWhite

0


Best Answer

Look at the motor nameplate and it shoud have the amp draw on it. If the nameplate is missing, then the amp draw depends on what type of motor it is.

The basic calculation to get you in the ball park would be as follows:

1 HP = 0.75 KW

7.5 HP = 5.63 KW

Assume the efficiency of the motor is 80%, then the power supplied will need to be 5.63/0.8 = 7.04 KW

amp draw = 7040/220 = 32 amps

<<>>

For calculation purposes the electrical code book states that a 7.5 HP motor draws 40 amps.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps does 1 phase 220volt 7.5 HP draw?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many amps does a 10kw heater draw that's 3phase 220volt?

To calculate the amperage for a 10kW heater on a 3-phase 220V system, use the formula: Amps = (kW x 1000) / (√3 x Volts). So, Amps = (10 x 1000) / (√3 x 220) = 26.18 amps per phase. Therefore, the total current drawn by the heater is 26.18 amps per phase multiplied by 3, which equals approximately 78.54 amps.


How many amps at 415volt is 80amps at 220volt?

X / 415 = 80 / 220 = 151 amps


How many amps does a 2000 watt heater draw at 240 volts on each line?

For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.


How many amps for 1hp 3phase?

For a 1hp 3-phase motor, the current draw will depend on the voltage supply. Typically, at 230V, a 1hp 3-phase motor will draw around 3.6 amps. However, this value may vary based on the motor efficiency and power factor.


How many amps does a 1 phase heater draw if it run on 8kw?

To answer this question the voltage of the heater must be given. I = W/E.


How many amps does a 3 phases 600 volt 10 hp draw?

Assuming the power factor is 1, a 10 hp motor operating at 600 volts in a three-phase system would draw approximately 13.33 amps.


How many amps does a 5 hp 208 volt 3 phase motor draw?

read the name plate on the motor


How many amps does 30KW strip heater draw at 208 volts 3PH?

To calculate the current draw, use the formula: Current (A) = Power (W) / (Voltage (V) * √3). Plugging in the values, we get Current = 30000W / (208V * √3) ≈ 78.7A. So, a 30KW strip heater operating at 208 volts 3-phase would draw approximately 78.7 amps.


How many amps does a 1.5 hp 230v 3 phase motor draw?

For a 1.5 hp 230v 3 phase motor, you can calculate the amperage using the formula: Amps = (HP x 746) / (Volts x Efficiency x Power Factor x √3). Assuming an efficiency of 0.85 and a power factor of 0.8, the amperage draw would be approximately 4.3 Amps.


How many amperes for 3 phase 220v 5 tonner?

50 Amps Single Phase 20 Amps Three Phase


How many amps does a 208 volt 3 phase 45 kw hot water heater draw?

To calculate the amperage, you can use the formula: Amps = (kW × 1000) / (√3 × Volts). Plugging in the values, we get: Amps = (45 × 1000) / (√3 × 208) ≈ 131.1 amps. So, the hot water heater would draw approximately 131.1 amps.


How many amps per phase would a machine rated at 460 amps over three phases take?

It depends on the internal circuit of the machine. If it is star operated its full load current will be same as rated current. If it is Delta operated its full load per phase current will be as given below : Phase current = Line Current / 1.732