MVA is the apparent power. MVA=( MW+ MVAr)1/2
MVA= square root of (MW2 + MVAR2 )
There are two concerns here regarding loading on transformers of this size. First is the difference between MVA and MW. MW is just real power -- watts. MVA is total power which includes real power (MW) and reactive power (MVAR).--- http://en.allexperts.com/q/Electric-Power-Utilities-2405/operation-limit-oof-power.htm
MVA(Mega volt ampere) is the cos component of MW. So one should know the power factor of the system for conversion from MVA to MW.
Large transformers are filled with oil which circulates to a radiator to get rid of excess heat. A 100 MVA transformer should waste about 1 MW of power on full load, 0.5 MW on no load.
MVA is the apparent power. MVA=( MW+ MVAr)1/2
By definition, MVA is equivalent to the vector sum of MW and MVAR: MVA^2 = MW^2 + MVAR^2 = 2500 MVA = 50
MVA= square root of (MW2 + MVAR2 )
There are two concerns here regarding loading on transformers of this size. First is the difference between MVA and MW. MW is just real power -- watts. MVA is total power which includes real power (MW) and reactive power (MVAR).--- http://en.allexperts.com/q/Electric-Power-Utilities-2405/operation-limit-oof-power.htm
No, mvar (megavolt-ampere reactive) is a unit of apparent power while MVA (megavolt-ampere) is a unit of real power. Mvar is used to measure reactive power, while MVA is used to measure total power (both real and reactive).
mw is the unit of real power and mvar is unit of reactive power. You should now the current and power factor angle to calculate the voltage.p=vi cos piq=vi sin piAnswerI think you mean MW, not mw -capital 'M' mega; lower-case 'm' milli!!! And the symbol for watt is a capital 'W', not a lower case 'w'. Also, I think you mean 'Mvar'(mega, not milli!).
You would have to know the Power Factor, normally designated PF. MVA x PF = MW. If the PF is unity then MVA = MW. A PF of UNITY suggest the load is purely resistive with neither capacitive nor inductive components in the load or source. Of course this can mean such components have been balanced artificially.
MVA(Mega volt ampere) is the cos component of MW. So one should know the power factor of the system for conversion from MVA to MW.
Large transformers are filled with oil which circulates to a radiator to get rid of excess heat. A 100 MVA transformer should waste about 1 MW of power on full load, 0.5 MW on no load.
1 mw = 4tph
You would have to know the Power Factor, normally designated PF. MVA x PF = MW. If the PF is unity then MVA = MW. A PF of UNITY suggest the load is purely resistive with neither capacitive nor inductive components in the load or source. Of course this can mean such components have been balanced artificially.
1mva = 1000kva so you simply divide by 1000. 10000KVA = 10MVA K = kilo = 1000 M = mega = 1000000