answersLogoWhite

0


Best Answer

Amps = Watts/Voltage. 4500/240 = 18 amps. You would use a #12 copper wire which is rated at 20 amps. On a hot water tank there is only one of the elements on at a time. The incoming cold water is taken to the bottom of the tank through a pipe inside the tank. When the lower thermostat senses the cold water the lower element turns on. As you draw hot water from the top of the tank the cooler water from the bottom will rise. When the top thermostat senses the cool water it shuts off the bottom element and turns on the top element. When this water is heated to the tank set- point it shuts off and the lower element turns on to heat the rest of the water. When the total tank temperature is at the set point all elements turn off. By using this type of procedure there is always hot water at the top of the tank for use.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Your water heater has two 4500 watt elements what size wire should you use?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

How many amps does a 50 gallon water heater with 2-4500 watt elements draw?

30


Will a 5500 watt generator run a electric water heater?

The average size water tank is 4500 watts. The generator's supply will be large enough to operate the water tank. Larger tanks over 5000 watts will not heat correctly.


How is an electric water heater wired?

Hot water tanksAmps = Watts/Voltage. 4500/240 = 18 amps. You would use a #12 copper wire which is rated at 20 amps. On a hot water tank there is only one of the elements on at a time. The incoming cold water is taken to the bottom of the tank through a pipe inside the tank. When the lower thermostat senses the cold water, the lower element turns on. As you draw hot water from the top of the tank the cooler water from the bottom will rise. When the top thermostat senses the cool water it shuts off the bottom element and turns on the top element. When this water is heated to the tank set point it shuts off and the lower element turns on to heat the rest of the water. When the total tank temperature is at the set point all elements turn off. By using this type of procedure there is always hot water at the top of the tank for use.Actually, not all of this first answer is correct! A 4500 watt heater will draw around 18.75 amps. However, electric water heaters are considered "continuous loads". This means you can't load it's circuit more than 80%. So a 4500 watt heater circuit must be "sized up" to either a 25 amp or 30 amp circuit. This means that #10 copper wire will also be used. Now, a 3800 watt heater will draw around 15.8 amps. In this case, a 20 amp breaker and #12 copper wire can be used. Always check the heater's nameplate to be certain of it's ratings. The calculation used is correct.


What is the average monthly cost to operate an electric hot water tank?

Three hours is the average time to run the hot water per day so if you have a 1500 watt tank you will pay about $13.50 a month <<>> A 1500 watt water tank is not going to heat much water. The average home hot water tank operates with 4500 watt elements in it. To get an accurate price use 4500 watts as a starting point.


Does both elements on an electric water heater operate at the same time?

Hot water tanksAmps = Watts/Voltage. 4500/240 = 18 amps. You would use a #12 copper wire which is rated at 20 amps. On a hot water tank there is only one of the elements on at a time. The incoming cold water is taken to the bottom of the tank through a pipe inside the tank. When the lower thermostat senses the cold water, the lower element turns on. As you draw hot water from the top of the tank the cooler water from the bottom will rise. When the top thermostat senses the cool water it shuts off the bottom element and turns on the top element. When this water is heated to the tank set point it shuts off and the lower element turns on to heat the rest of the water. When the total tank temperature is at the set point all elements turn off. By using this type of procedure there is always hot water at the top of the tank for use.

Related questions

How many amps does a 50 gallon water heater with 2-4500 watt elements draw?

30


Can you replace a 4500 watt water heater with a 3800 watt water heater?

Yes, but realize that it will take longer to reheat water as it is used. In other words the recovery time will be a bit longer.


What ampts on the breaker do you needfor a 4500 watt hot water tank?

Assuming this is standard house voltage of 120 VAC your 4500 Watt heater will draw about 37.5 amps. You would normally install a 50A breaker and would have to run 8 gauge wire.


Will a 5500 watt generator run a electric water heater?

The average size water tank is 4500 watts. The generator's supply will be large enough to operate the water tank. Larger tanks over 5000 watts will not heat correctly.


How is an electric water heater wired?

Hot water tanksAmps = Watts/Voltage. 4500/240 = 18 amps. You would use a #12 copper wire which is rated at 20 amps. On a hot water tank there is only one of the elements on at a time. The incoming cold water is taken to the bottom of the tank through a pipe inside the tank. When the lower thermostat senses the cold water, the lower element turns on. As you draw hot water from the top of the tank the cooler water from the bottom will rise. When the top thermostat senses the cool water it shuts off the bottom element and turns on the top element. When this water is heated to the tank set point it shuts off and the lower element turns on to heat the rest of the water. When the total tank temperature is at the set point all elements turn off. By using this type of procedure there is always hot water at the top of the tank for use.Actually, not all of this first answer is correct! A 4500 watt heater will draw around 18.75 amps. However, electric water heaters are considered "continuous loads". This means you can't load it's circuit more than 80%. So a 4500 watt heater circuit must be "sized up" to either a 25 amp or 30 amp circuit. This means that #10 copper wire will also be used. Now, a 3800 watt heater will draw around 15.8 amps. In this case, a 20 amp breaker and #12 copper wire can be used. Always check the heater's nameplate to be certain of it's ratings. The calculation used is correct.


What is the average monthly cost to operate an electric hot water tank?

Three hours is the average time to run the hot water per day so if you have a 1500 watt tank you will pay about $13.50 a month <<>> A 1500 watt water tank is not going to heat much water. The average home hot water tank operates with 4500 watt elements in it. To get an accurate price use 4500 watts as a starting point.


Does both elements on an electric water heater operate at the same time?

Hot water tanksAmps = Watts/Voltage. 4500/240 = 18 amps. You would use a #12 copper wire which is rated at 20 amps. On a hot water tank there is only one of the elements on at a time. The incoming cold water is taken to the bottom of the tank through a pipe inside the tank. When the lower thermostat senses the cold water, the lower element turns on. As you draw hot water from the top of the tank the cooler water from the bottom will rise. When the top thermostat senses the cool water it shuts off the bottom element and turns on the top element. When this water is heated to the tank set point it shuts off and the lower element turns on to heat the rest of the water. When the total tank temperature is at the set point all elements turn off. By using this type of procedure there is always hot water at the top of the tank for use.


What is180 multiplied by 25?

If you have a calculator, you should get the answer 4500.


What is 4500 times 200000000?

Your answer should read :- 900,000,000,000


How much water do fish drink in a day?

4500 million letres


How much water a fish drinks in a day?

4500 million letres


How much water does a 15x48 pool hold?

around 4500 gallons