The current should be listed on the motor nameplate as FLC or FLA (full load current/full load amps). Starting current is listed as LRC (locked rotor current). However, to calculate current for any load, divide watts by voltage. 1 hp = 746 watts 85 hp = 63410 watts 63410 watts / 208volts = 304.85 amps 63410 watts / 480 volts = 132.10 amps

User Avatar

Wiki User

15y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

11y ago

There are two ways to find the amperage and both are not accurate as reading the amperage off of the motor's nameplate. The first is by wattage. 1 HP equals 746 watts. 746 x 3 = 2238. Amps = W/V. 2238/230 = 9.7 amps. The second is from the electrical code book which states that a 3 HP motor at 230 volts draws 17 amps. It also states that this amperage is only to be used as a guide. Submersible pumps are supposed to have a stainless steel plate that comes with the pump. This plate should be in the pump house and be readily available if pump information is needed. Look for motor information on the pump controller, sometimes the information label is stuck onto the inside of the controller cover plate. Of the two amperage's I would go with the 9.7 amps. A very accurate way of measuring the amperage is to use a clamp on amp meter. These test instruments can measure the actual ccurrent flow when the motor is operating. If you have an electrician friend ask him to measure the amperage.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is the amperage draw of a 3 H P submersible pump motor 230 volts single phase?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

What is the amperage of a 20 HP 240v single phase motor?

Typically single phase motors go up to 10hp. Wouldn't be very efficient at about 100 amps. A 20hp 3 phase motor at 230v pulls 52 amps. The 10hp single phase 230v pulls 50 amps.


Why doesn't a shunt motor operate on a single phase AC supply?

Shunt motors do operate on single phase AC. There are millions, if not billions of them worldwide running right now.Make certain your voltage supply is correct for your motor. Also, make certain you're providing the proper amperage. Make sure it's not a three phase motor. (three phase motors won't operate on single phase power.) If your supply voltage and amp supply is correct and the motor still doesn't run, you've got a bad motor.


What is the difference between a one phase and a three phase motor. And if a three phase motor is given a single phase supply will it run or not?

The difference between a single phase and a three phase motor is the amount of power conductors that feed the device. As to the other part of the question a three phase motor will not start or run on single phase. The phase angles on three phase are 120 degrees apart on a single phase system they are 180 degrees apart.


What is the full load running current of a 3hp 208volt single phase continuous duty ac motor?

It would probably be 20-30 amps. <<>> The electrical code book states a value of 18.7amps for a 3HP 208 volt motor. If the nameplate data is available it is always best to use it when calculating wire size and overload protection for the motor.


Drawing block diagram of single phase capacitor start motor?

Drawing block diagram of single phase capasitor start motor?

Related questions

What is the amperage of a 20 HP 240v single phase motor?

Typically single phase motors go up to 10hp. Wouldn't be very efficient at about 100 amps. A 20hp 3 phase motor at 230v pulls 52 amps. The 10hp single phase 230v pulls 50 amps.


Why doesn't a shunt motor operate on a single phase AC supply?

Shunt motors do operate on single phase AC. There are millions, if not billions of them worldwide running right now.Make certain your voltage supply is correct for your motor. Also, make certain you're providing the proper amperage. Make sure it's not a three phase motor. (three phase motors won't operate on single phase power.) If your supply voltage and amp supply is correct and the motor still doesn't run, you've got a bad motor.


How do you check single phase motor winding?

Single phase motor winding is often checked just by listening to the noise that the motor is making. An experienced person can tell if the motor is working at single phase or double phase.


How many Amps for 3 horsepower at 208 volts?

For a single phase 3 HP motor at 208 volts the amperage is 18.7 amps. For a three phase 3 HP motor at 208 volts the amperage is 10.5 amps. This figure is derived at by taking the full load amps at 230 volts and adding 10%. As the voltage goes down the amperage goes up. For 200 volt motors 15% is added to the FLA of a 230 volt motor.


Is 3 phase motor run on 1 phase supply?

No. That would be a single phase motor.


How do you define the amperage on a single phase 75kva transformer?

please show me how to figure it out.


What is the difference between a one phase and a three phase motor. And if a three phase motor is given a single phase supply will it run or not?

The difference between a single phase and a three phase motor is the amount of power conductors that feed the device. As to the other part of the question a three phase motor will not start or run on single phase. The phase angles on three phase are 120 degrees apart on a single phase system they are 180 degrees apart.


How do you convert a 0.37kw 4 pole 3 phase motor to single phase?

The motor cannot be altered to work on single phase power. You will either have to put in a new single phase motor or use a phase convertor box. Do a google search for phase convertor - you will find plenty.


You have one hp three phase motor where as available power supply is only single phase how can you run this motor?

You will need to install a phase converter or change the motor to single phase. You can find a licensed electrician at www.contraxtor.com


How do you reverse single phase ac motor to generator?

how reversing an ac single phase induction motor to wark as induction generator


How do you connected 3 phase motor to single phase power?

Use VFD to make 3 phase from single phase source.