answersLogoWhite

0


Best Answer

The reading of 14.65 on the 20k setting means 14.65K Ohms, and you probably need to go back and re-read the instructions for the meter. If, for instance, you used a 2M scale, if you had one, you would get 0.014, but the result would not be very accurate, as you need to pick a range that is close to maximum reading for that range.

It is normal procedure to start with a high range and come down in range as you approach an on scale reading.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What does 14.65 ohms equal on the 20k setting. I got no reading on the lower settings?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

Why two psv installed on column or vessel?

PSV stands for Pressure Safety Valve Both of them are set at slightly different pressure settings. If the pressure in the vessel is too high it will trigger the PSV with the lower setting first. If this is not sufficient, than the second one will open. Just like a failsafe.


What ohms setting do you use on a meter for 240v electric heater?

Whenever you use an ohmmeter, you must first ensure that the device you want to test is disconnected from the supply. So the fact that your heater is rated at 240 V is irrelevant to this question. The heater must be disconnected from the supply BEFORE you contemplate measuring its resistance. Which 'ohms setting' to use is then simply determined by whichever setting gives you the best reading. For an analogue ohmmeter, this is whichever setting results in the pointer being towards the lower-resistance end of the scale.


What effect if any does connecting an ammeter in series with a resistor in a circuit have on the current through resistor?

The Amp meter was design to allow current flow through the meter to measure with a minimal alteration to the original circuit. That is the ideal world, in reality the meter has some resistance and will lower the current flow. The multiple current setting on most meter will reduce the effects caused by the meter but you must be careful not to damage the meter by reading to high for the setting.


What happens when two circuit breakers are parallel?

There are 3 cases in C.B. paralleling: 1. Both Circuit breakers of same current ratings with same time settings. 2. Both circuit breakers of different current ratings 3. Both Circuit breakers of same current ratings with different time settings. Case1: Any of the C.B.trips (depending on CT characteristics as no two CTs' can have same characteristics) Case 2. The one with lower current ratings would trip first. Case 3: The one with lower time settings would trip earlier.


Why phase fault relays are having higher settings and more plug positions while earth fault relays are having lower settings and usually only two plug positions?

phase fault relay are having higher settings because the magnitude of phase fault currents are not so much higher as earth fault currents.hence in order to prevent any damage to the system,the earth faults should vanish as quickly as possible

Related questions

What is wrong with your Climate control heater works only on full power setting but not on automatic or lower settings Vectra CDX?

Defective heater blower motor resistor pack.


How to lower graphics of a game before I run it because I can't run it it is on too good performances for my PC?

A person can lower the graphics of a game before they run it by accessing the setting option before the game begins. A person may also lower the graphics through their video card settings.


Which symbol I orII on my Rival crock pot is High and which is low?

The temperature settings on a Rival Crock-Pot are listed by increasing temperature meaning that the high setting is represented by the higher numeral and the low setting is represented by the lower numeral. So, "I" means low and "II" means high.


Do driveway alarms have different setting for their loudness?

Some driveway alarms have different settings allowing for the adjustment of loudness. The more expensive driveway alarms allow one to adjust the receiver to lower the sound that is emitted.


Why a hair dryer has a high- heat setting with a lower resistance than the low-heat setting?

Because a higher resistance would have resulted in more heat loss, but the higher is he current, the more energy is lost to heat. Therefore, a lower resistance would release more heat.AnswerPower is equal to voltage squared divided by resistance. So, for a given voltage, the lower the resistance the higherthe power.


What divides the lower half of the data into two equal parts?

The lower quartile divides the lower half into two equal parts.


Settings of the servant girl story?

The setting of the servant girl story is typically a historical or period setting, such as a manor house or estate in the 19th century. The story often takes place in a hierarchical society where the servant girl occupies a lower social status than her employers. The setting helps to establish the power dynamics and tensions that drive the plot.


What does a lower decibel reading say about the sound waves energy?

Lower decibels correlate to lower energy.


How did the distance of the sensor from the electromagnet affect the reading on the sensor?

the greater the distance the lower the reading


When rainfall what is the reading on the pH scale lower than 5.6?

if rainfall has reading on the pH scale lower than 5.6 it is called Acid Rain.


Your World of Warcraft game is slow what do you do?

Lower your in-game video settings.


How do you increase the video memory?

Lower the quality setting.