This vector group test is done to confirm whether the vector group provided in the name plate is correct or not and also to confirm that the winding has not been damaged during transport, installation and erection.

Taking a particular example, for Dyn11 transformer we have to apply 3~ 400v to the primary, with primary 'U' & secondary 'u' shorted....

then check the voltage across different terminals such as V-v, V-w, W-w, W-v

for Dyn11 configuration (V-v = V-w = W-w)less than W-v....

you can compare the results after drawing the vector diagram for the same......

the purpose of shorting the primary U & secondary u is to nullify the phase shift, to obtain a reference vector...

User Avatar

Wiki User

8y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

12y ago

Zigzag is the special kind of winding which has both delta and star connection.It has two coils, one coil is connected as a delta and another coil has a star point as Neutral and give to Earth through Neutral earthing resistor.

Procedure of vector group testing:

1. Ensure the system is isolated or not and remove the earthing from the System.

2. Make shot between HV R-Phase and LV R-phase of the Transformer.

3. Apply 3 phase supply to the HV of the Transformer.

4. Measure the combinations of voltages between HV and LV sides compared with the vector diagram.

5. Make sure the combinations are correct or not.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How can you test ZNyn11 Vector group transformer?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

Using vector to add objects and display their member variables?

import java.util.Vector; suppose-:::: test t=new test(); /**this is how we add elements to vector*/ Vector v=new Vector(); v.addElements(t);


Why the open and short ckt test of transformer is needed?

The open/short-circuit test on a transformer isn't 'needed'. It's only used if you want to find out the efficiency of a transformer.


What is the use of back to back test in transformer?

Back to back test give data for finding the regulation , efficiency and heating under load condition. Back to back test is performed in the presence of two identical transformer. In this test one transformer remains open and other remains loaded. Hence sumpner's back to back test is generalised form of o/c test and s/c test which is performed within one test only. Hence from this test we find core loss and full load copper loss simultaneously at a time.


Can a high voltage transformer be megged with a megger meter?

No. A megger's output voltage is not high enough to test the insulation of a high-voltage transformer if, by 'high-voltage transformer ', you mean a distribution transformer or power transformer. Instead, a high-voltage test set or 'pressure tester' (e.g. a 'HiPot' tester) must be used, as these produce far higher voltages.


What types of transformer tests are there?

there are various types of trasformer tests are here Open Ckt test Short ckt test IR value test Vector group test Phase sequence test Magnetizing test turn ratio test T/f oil insulation breakdown test and so on............

Related questions

How do you test Yyn0 vector group of transformer?

in electrical engineering


What are precommissioning tests of transformers?

magnetising current test, magnetising balance test, s.c test, vector group test, winding resistance test, ratio test


What is dielectric test in transformer?

why need dielectric test for transformer


How will be conduct test on transformer?

Short circuit test and open circuit test are widely used to test the efficiency of the transformer.


What are the purposes of performing no load test for the transformer?

These two tests are performed on a transformer to determine (i) equivalent circuit of transformer(ii)voltage regulation of transformer(iii) efficiency of transformer. The power required for theseOpen Circuit test and Short Circuit test on transformeris equal to the power loss occurring in the transformer.


Using vector to add objects and display their member variables?

import java.util.Vector; suppose-:::: test t=new test(); /**this is how we add elements to vector*/ Vector v=new Vector(); v.addElements(t);


Why the open and short ckt test of transformer is needed?

The open/short-circuit test on a transformer isn't 'needed'. It's only used if you want to find out the efficiency of a transformer.


Does vector marketing drug test?

no


What is the purpose of conducting sc and oc test of single phase transformer?

to determine the transformer characteristics...


What is circuit diagram for ratio test of transformer?

Mechanauts


Procedure for sumpners test?

Procedure for sumpners test is the single phase transformer. This is a back to back test.


What is load test on single phase transformer?

A load test on a transformer is done to make sure it stays within its designed temperature range while on full load.