Best Answer

This is not recommended. The heater will operate at more than its given specified wattage. A 208 volt heater run off 220 volts will have an output increase by 11.87 percent. Similarly, a 220 volt heater can be run off of 208 but the wattage will be reduced by 10.61%. The calculations, using Ohms' Law, are shown below.

<><><>

Watts = volts x amps (W = V x I) and I = W / V so, if we take a 2000 watts heater designed to run on 208 volts, I = 2000 / 208 = 9.6 amps

Resistance = volts / amps (R = V / I) so the heater's resistance is 208 / 9.6 = 21.632 ohms

Amps = volts / resistance (I = V / R) so, running on 220 volts, I = 220 / 21.632 = 10.17 amps

W = 220 x 10.17 = 2237 watts, which is an increase of 2237/2000 = 11.87%.

<><><>

W = V x I and I = W / V so, if we take a 2000 watts heater designed to run on 220 volts, I = 2000 / 220 = 9.09 amps

R = V / I so the heater's resistance is 220 / 9.09 = 24.2 ohms

I = V / R so, running on 208 volts, I = 208 / 24.2 = 8.595 amps

W = 208 x 8.595 = 1787.76 watts, which is a decrease of ( 2000-1787.76 ) / 2000 = 10.61%.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

11y ago

Yes

<<>>

The heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced.

For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.

W = watts, I = amperage, R= resistance in ohms and E = voltage.

This answer is:
User Avatar

User Avatar

Wiki User

10y ago

The voltage range that the heater can handle should be marked on the case. The supply voltage must be within that range. Do not run on excessive voltage because the amount of heat produced could be dangerous.

<<>>

208 volt heater on 240 volts

The heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced.

For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.

W = watts, I = amperage, R= resistance in ohms and E = voltage.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you use 240 volts for a 208 volt heater?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

What is the maximum volts that can be used on a 208 230 volt motor?

You should not go above 240 volts for that type of motor.


Will a 208 volt 3 phase equipment work on 240 volt 3 phase?

Yes but a 208 volt heater is intended to be delta connected so there are only three terminals. The three heating elements could be rewired to run in parallel off a 220 v single phase circuit, and the heater would then operate at 12% excessive power, which might shorten its life. &lt;&lt;&gt;&gt; No. The heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced. For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating. W = watts, I = amperage, R= resistance in ohms and E = voltage.


Can you connect 208 volt equipment to 240 volts?

Electricity is NOT clean, meaning, it is not 208, 220, or even 240. It usually varies and spikes. The problem with the lights, is likely because it's cold in your shop. Florescent lights do not perform well in the cold. (or they might be getting old).However, you can test your "average" voltage coming in with your vom (volt omm meter, set on the 240 volt setting).However, the very existence of surge protectors should give you a clue about the consistency of electrical voltage.208 volt equipment on 240 voltsThe heater will operate over its given specified wattage. Equipment rated for 208 volts and operated on 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit.For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.W = watts, I = amperage, R= resistance in ohms and E = voltage.


Can you run a 208 volt device on 240 volts?

The device should be marked with the voltage range it works over. If the device is run at a voltage above that range it could be dangerous or the device could be damaged &lt;&lt;&gt;&gt; 208 volt device on 240 volts No. The device will operate over its given specified wattage rating. A 208 volt device run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced. For example lets use a baseboard heater. If the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating and could destroy the equipment.. W = watts, I = amperage, R= resistance in ohms and E = voltage.


Can a 277 unit heater be supplied with 240 volts?

Absolutely not!! 277 volts is developed from a 480 volt power supply employing 1 conductor and a neutral. 240 volt power comprises two hot conductors and NO neutral.

Related questions

What is the maximum volts that can be used on a 208 230 volt motor?

You should not go above 240 volts for that type of motor.


What is a 208 circuit?

The 208 volt configuration is one phase of a three phase source at 240 volts, where the 208 volt circuit is connected between the center tap of one 240 volt phase (usually a grounded neutral, in the style of a standard 120/240 split phase system) and the high delta connection on either of the other two phases. 208 circuit would consist of two phases of a 208 volt wye system or could be all three phases. The voltage between conductors would be 208 volts. The voltage to ground from any phase would be 120 volts. A 240 volt delta system would give you a high leg to ground, somewhere around 190 volts and the other two would be 120 volts to ground.


Will a 208 volt 3 phase equipment work on 240 volt 3 phase?

Yes but a 208 volt heater is intended to be delta connected so there are only three terminals. The three heating elements could be rewired to run in parallel off a 220 v single phase circuit, and the heater would then operate at 12% excessive power, which might shorten its life. &lt;&lt;&gt;&gt; No. The heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced. For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating. W = watts, I = amperage, R= resistance in ohms and E = voltage.


Can you connect 208 volt equipment to 240 volts?

Electricity is NOT clean, meaning, it is not 208, 220, or even 240. It usually varies and spikes. The problem with the lights, is likely because it's cold in your shop. Florescent lights do not perform well in the cold. (or they might be getting old).However, you can test your "average" voltage coming in with your vom (volt omm meter, set on the 240 volt setting).However, the very existence of surge protectors should give you a clue about the consistency of electrical voltage.208 volt equipment on 240 voltsThe heater will operate over its given specified wattage. Equipment rated for 208 volts and operated on 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit.For example if the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.W = watts, I = amperage, R= resistance in ohms and E = voltage.


Can you run a 208 volt device on 240 volts?

The device should be marked with the voltage range it works over. If the device is run at a voltage above that range it could be dangerous or the device could be damaged &lt;&lt;&gt;&gt; 208 volt device on 240 volts No. The device will operate over its given specified wattage rating. A 208 volt device run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced. For example lets use a baseboard heater. If the heater is 5000 watts at 208 volts, the current is I =W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) =5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating and could destroy the equipment.. W = watts, I = amperage, R= resistance in ohms and E = voltage.


Do all electric ovens cooktops ranges and clothes dryers operate on 208v as well as 240v?

No, use only the voltage for the appliance that your utility system is supplying to your residence. If your system is 208 volts use 208 volt appliances. Likewise if the utility system is 240 volts use only 240 volt appliances. 208 appliances on 240 will overheat the appliances and 240 appliances on 208 will not produce the wattages that the manufacturer recommends for cooking and drying.


Can i run a 240 volt water heater on 120 volt?

No. A water heater requires a 240 volt connection and cannot be re-wired to run on 120 volts. There isn't enough amperage in 120 volts to power the heating rods that are inside.


Can a 277 unit heater be supplied with 240 volts?

Absolutely not!! 277 volts is developed from a 480 volt power supply employing 1 conductor and a neutral. 240 volt power comprises two hot conductors and NO neutral.


Do you need a step down transformer to run a 208 volt steam table on 240 volt feed?

Yes a transformer should be used. The steam table needs its correct voltage otherwise on 240 volts it will operate over its given specified nameplate wattage. A 208 volt heating element run off of 240 volt will have an output increase by 75 percent.


Can 240 volt appliances from NZ run on 240 Volts in the US?

yes 240volts is 240 volts


Is it possible to hook up a unit that is 208 volt single phase to a 240 volts 3 phase?

Any two legs of a three phase system are classed as single phase. If a 208 volt device is connected across two legs of a 240 volt system its current draw will be higher. It is not recommended to connect a 208 volt device to a 240 volt supply. Using a constant resistive load of 6000 watts for an example, the resistance of the unit at 208 volts has to be found. R = E (squared)/W = 7.21 ohms. Now using the formula to find amperage at this resistance I = E/R, 208/7.21 = 28.84 amp at 208 volts. If the 208 volt device is connected to a 240 volt supply the following condition happens. I = E/R, 240/7.21 = 33.29 amps. The device in now definitely overloaded and instead of its rated 6000 watts it is outputting W = A x V, 33.29 x 240 = 7989 watts almost 2000 watts more than the unit is rated at.Using a 240 volt rated device on 208 volts is more forgiving and is done quite often. Using the same 6000 watts on 240 volts the resistance is calculated to be R = E (squared)/W = 9.6 ohms. If the 240 volt device is connected to a 208 volt supply the following condition happens. I = E/R, 208/9.6 = 21.67 amps. To check this connection's wattage W = A x V, 21.67 x 208 = 4507 watts or about 1500 watts below its rated output at 240 volts.If the connected load is a constant wattage like a motor, the amperage and voltage will change to maintain the constant wattage. I = W/E. A motor rated at 6000 watts at 240 volts will draw 25 amps. A motor rated at 6000 watts at 208 volts will draw 28.8 amps.The CEC states that if a 208 volt rated motor is connected to a 240 volt supply its full load current has to be increased by 10 % for its overload protection.If the three phase source is delta connected, and the neutral/ground is at the center tap of one of the phase windings, then there is 208 volts available from neutral to the third phase leg. In this case, there would be no mismatch of voltage, and the 208 volt load will operate as designed.This particular configuration is not so common. It is sometimes used in a light industrial setting where a fourth transformer for the 120/240 split phase portion is not used - it provides 240 three phase delta only, 120/240 split single phase, residential style, and 208 single phase.See related links below (High Leg Delta)Note that 240 three phase loads are also not so common. In the case where 480 three phase is required in this configuration, then there is a step up transformer trio provided, ususally by the customer.


How many volts can b drawn off a 240 volt breaker?

240 volts maximum.