answersLogoWhite

0


Best Answer

You will not pull enough power to properly operate the appliance, and you can damage the electric assembly possibly nullifying the warranty. It won't work very well. You need to get a 220 breaker, which goes across both legs of the 220 panel as opposed to a 110 v breaker which only pulls current from ONE leg of the 220 line. But it won't burn out anything if you only connect it to 110.

User Avatar

Wiki User

17y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

If it's a true 120 V only appliance, and not a dual-use appliance it will most likely break immediately. There may be a fuse in the unit, which can be replaced the unit to get it working(with the right voltage) again, or the unit may be permanently destroyed.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

208 volt heater on 240 volts

The heater will operate over its given specified wattage. A 208 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 208 but the wattage will be reduced.

For example if the heater is 5000 watts at 208 volts, the current is I = W/E 5000/208 = 24 amps. The resistance of the heater is R = W/I (squared) = 5000/24 x 24 (576) = 8.68 ohms. Applying 240 volts on the same heater whose resistance is 8.68 ohms results in this new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/8.68 = 6636 watts. This is 1636 watts higher than the manufacturer's safety rating.

W = watts, I = amperage, R = resistance in ohms and E = voltage.

This answer is:
User Avatar

User Avatar

Wiki User

10y ago

If the supply is well protected , the circuit breaker will trip. If your wiring is old & of poor insulation , there could be an electrical fire somewhere in the wiring. assuming that the power wires & the supply outlet are capable of handling the power drawn & the heater is robust enough it will run for some time at double its rated capacity .

However since the temperatures will be considerably higher than normal operation, the weakest or the hottest part on the heater will burn out akin to a fuse. The cheaper the heater the faster the burnout time, which could be for practical purposes almost instantaneous.

<<>>

120 volt heater on 240 volts

The heater will operate over its given specified wattage. A 120 volt heater run off of 240 volt will have an output increase. Ohms law stated that current is directly proportional to the applied voltage and inversely proportional to the resistance of the circuit. A 240 volt heater can be run off of 120 volts but the wattage will be reduced.

For example if an ordinary 1000 watt baseboard heater's supply is 120 volts, the current of the heater will be, I = W/E 1000/120 = 8.3 amps.

The resistance of the heater is R = W/I (squared) =1000/8.3 x 8.3 (69) = 14.5 ohms.

Applying 240 volts on the same heater whose resistance is 14.5 ohms results in a new heater wattage rating. W = E (squared)/R = 240 x 240 (57600)/14.5 = 3972 watts.

This is 2972 watts, almost 300%, higher than the manufacturer's designed safety rating.

The amperage drawn by connecting a 120 volt, 1000 watt heater to a 240 volt source will be, I = W/E = 3972/120 = 33 amps.

W = watts, I = amperage, R = resistance in ohms and E = voltage.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

It gets hot very quickly. If the internal thermal protection device doesn't trip then most likely the breaker will. e.g. 1000 watt heater. Normal current for the heater at 120 volts is 8.3 amps. To find the resistance of this heater use the formula R = E sq/W. 120 x 120/1000 = 14.4 ohms resistance. Now for the current at 240 volts, I = E/R. I = 240/14.4 = 16.6 amps. As you can see you will be introducing double the current to the 120 volt heater. Ohms law states, the current is directly proportional to the applied EMF (voltage) and inversely proportional to the resistance of the circuit.

This answer is:
User Avatar

User Avatar

Ralph Carter

Lvl 2
4y ago

All those answers that use a static resistance value are incorrect. A heating element starts with a low resistance and the resistance increases as the element heats up. With the higher voltage applied the resistance increases to the point where the rated heater output is obtained. It then is self limiting due to the increasing resistance with temperature increases. The heating element composition, length, and surrounding cooling forces, will determine the effective resistance of the element with a specific applied voltage. This will not be as hot with a lower voltage but the actual temperature is typically not a linear function.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What will happen if you plug in a heater 120 volts to 240 volts?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What do you plug a block heater into?

plug a block heater plug into any household 120 electrical outlet just like plugging in a heater in your house


Can i run a 240 volt water heater on 120 volt?

No. A water heater requires a 240 volt connection and cannot be re-wired to run on 120 volts. There isn't enough amperage in 120 volts to power the heating rods that are inside.


Can you plug your 120v magic bullet blender to a 220 outlet?

No, in North America the plug configuration will not allow that to happen. The blade configuration for 120 volts are in parallel where as the 220 volt configuration are in tandem.


Can you plug a 220 hair dryer into a 230 plug?

Nominal residential voltage is 120/240 volts. Not sure from you description if the plug is just rated at 230 volts or is supplying 230 volts (It is likely that the plug may be rated at 230 volts, but only operating at 120 volts). A typical hand held hair dryer would operate on 120 volts. A commercial hair dryer might operate at 220 volts, but must be plugged into a 220 supply.


If an electric heater has a red blue and green wire that has been cut off how do i know if its 120 volts or 240 volts?

A label.


Can you plug a 120 volts 60 Hz into 250 Volt wall socket?

NO


Can you run one 1500 watt heater on a 125V- 15A 60Hz power strip?

Yes, a 1500 watt heater operating on 120 volts has an amperage of A = W/V. Amps = Watts/Volts = 1500/120 = 12.5 amps. It is not a recommended practice to do so.


Can you install a 120V baseboard heater on 110 amp power service?

Yes. The voltage of 120 volts is a nominal figure. The utility company has a plus or minus tolerance from 110 to 120 volts. This tolerance is based on the figure of 115 volts.


Is it safe to plug 120 volts to 130 volts outlet?

Yes- 120 volts is just the label given to it for ease of the consumer. The voltage actually fluctuates several times every second, and can reach as high as 175.


What gauge wire you would use to wire a 5kw heater hvac?

At 120 Volts you would draw about 42 amps. At 240 Volts it would be about 21 amps. For 120 Volts you would need 6 AWG and for 240 Volts you would need 10 AWG.


How can you plug in a 120 volt 1500 watt space heater in Korea?

Take the plug in your hand, and insert the plug into the wall outlet.


What is 50 percent of 120 volts?

50% of 120 volts = 50% * 120 = 0.5 * 120 = 60 volts