That distance you are going to have to install a sub-panel and run AWG # 4 wire and even then you will have a voltage drop of 7.45 volts giving you 232.55 volts at the sub-panel which is acceptable.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

10y ago

At 100 feet you are safe with AWG # 10 copper.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

A #6 copper conductor will limit the voltage drop to 3% or less when supplying 30 amps for 460 feet on a 240 volt system.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

10 AWG

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire for 30 amp breaker 240 volts 100 feet?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Can 10-2 wire carry 220 volts?

Yes as long as you use the correct size breaker.


What size breaker do you need for 5.7kw neff oven?

A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.


What size breaker do you need for two 60W bulbes 110 volts?

It is not the number of bulbs that you worry about. It is the wire size that is your concern. If the circuit is wired with AWG 12/2 wire then use a 20 amp breaker. If it is wired with a AWG 14/2 wire then use a 15 amp breaker. You are protecting the wiring with the correct size breaker.


How do you wire a wire to a wire?

If you are connecting 120 volts, you connect the black wire to the breaker, white wire to the neutral bar, and ground wire to the ground bar. If you are connecting 240 volts connect the black & white wires to the breaker, & ground wire to the ground bar.


What size amp breaker you need for a ac and a heater unit?

The sizing of a breaker is dependant upon the size of the wire it protects. The size of the wire is dependant upon what the load current in amps is. Without the amperage and wattage and the voltage of the appliances an answer can not be given. W = A x V, Amps = Watts/ Volts.


When installing a circuit breaker do you size the breaker to correct wire size or the device its controlling?

When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.


What size wire needed for 25 amps 220 volts for 75 feet?

10 AWG in copper.


What size wire and breaker do you need to run a 9000max watt generator?

If it is a portable generator the breaker should be self contained within the generators panel. If the generator is a stationary standby unit a voltage has to be stated to calculate the conductor size and hence the breaker size to protect the conductor. Amps = Watts/Volts.


What size breaker does it take to run a outdoor well?

Normally AWG #10 wire on a 30 amp breaker but it really depends on the size of the pump. The pump manufacture will specify the size wire and size breaker needed.


What size wire and breaker do you need for a 5000 watt garage heater?

Look on the heater and see what amps it is pulling. That will determine the wire size and breaker size. It must be on a dedicated circuit. 15 amps = AWG # 14 wire with 15 amp breaker 20 amps = AWG # 12 wire with 20 amp breaker 30 amps = AWG # 10 wire with 30 amp breaker 40 amps = AWG # 8 wire with 40 amp breaker


What size breaker needs to be installed for 15000 watt 240 volt heater?

15,000 watts at 240 volts will use 62.5 amps. Therefore you will need to use AWG #3 wire on a 100 amp breaker.


What size wire do you need to wire a 200 am breaker box?

6