The General rule is 1 square millimeter of cable per 10 amps so in this case you would use the available 2.5 sq mm cable
12 AWG wire for typical residential use.
12 gauge.
Normally it is a 20 amp using AWG 12/2 gauge wire. But it really depends on what size wire is on that circuit. If it is white AWG 14 gauge then use a 15 amp breaker. If it is yellow AWG 12 gauge then use a 20 amp breaker.
12 gauge underground wire or if you think you will ever add any devices to this circuit use 10 gauge.
The wire size depends on how much current it will conduct.
You listed no gauge wire. This is the required breakers.14 gauge - 15 amp12 gauge - 20 amp10 gauge - 30 amp8 gauge - 40 amp
The size of the wire is stated by its gauge under American Wire Gauge. Six gauge wire is size 6 AWG.
15 amps
Use 8 gauge wire.
# 3 gauge
Normally it is a 20 amp using AWG 12/2 gauge wire. But it really depends on what size wire is on that circuit. If it is white AWG 14 gauge then use a 15 amp breaker. If it is yellow AWG 12 gauge then use a 20 amp breaker.
12 gauge underground wire or if you think you will ever add any devices to this circuit use 10 gauge.
Yes. It is abbreviated as AWG. For example, in residential wiring the size wire to use on a 15 Amp circuit would be 14 gauge or 14 AWG.
NEC states that all GFCI's require a 20 amp circuit, the wire size for a 20 amp circuit is 12 gauge.
The wire size depends on how much current it will conduct.
Wire gauge is used to determine the size wire needed to carry the correct amount of current for the job. It must be sized appropriately for the current in the circuit you are building.
You listed no gauge wire. This is the required breakers.14 gauge - 15 amp12 gauge - 20 amp10 gauge - 30 amp8 gauge - 40 amp
The size of the wire is stated by its gauge under American Wire Gauge. Six gauge wire is size 6 AWG.
12 gauge wire is used for household plugins, and 14 gauge wire is used for lights. So, 12 gauge is the size to use. But since a freezer has an electric motor, it is best to not plug anything else with a motor into the same circuit.