come in your line side of the gfci and out the load side and onto the next device,which will make it gfci protected.You can go as far as 3-6 depending on the inspecter having juridiction and the manufacture specs on the gfci device you bought.keep in mind that if it trips then all connected devices in that series will also trip
You need to know whether the outlet you want to change is on a 15 or 20 amp circuit.
If you don't know what that means, hire an electrician.
Purchase the appropriate GFCI outlet.
Read the directions thoroughly.
Shut off the electricity to the outlet at the breaker.
If you don't know what that means, hire an electrician.
Make sure the box is large enough to accommodate the larger size of the GFCI. This is very important.
If you don't know what that means, hire an electrician.
Follow the directions explicitly or the GFCI won't function properly.
Best answer to your question; hire an electrician.
Warning:
Some jurisdictions have special rules. In my town, for instance, you must be a licensed electrician if you are changing anything for someone else, or it is a commercial property. Also, though rarely enforced for something as simple as a GFCI outlet, you need a permit and an inspection. Bottom line on the last part is, that if you have a fire, and the fire department determines that the installation did not meet code, they will revoke your fire insurance coverage.
If it's a GFCI receptacle and the button is not resetting then change the GFCI outlet.
Yes, but you can feed multiple outlets from one GFCI outlet. Make the first outlet fed in the cicuit a GFCI. Search for GFCI outlet with Google, etc. and I'm sure you will find an explanantion of how. Most GFCI's come with instructions also.
In a word NO, that will not cause either GFCI to trip. The correct term is GFCI (Ground Fault Circuit Interrupter)
A load of 1600 watts should be placed on a 20 amp 120 volt GFCI outlet.
It is a Ground Fault Circuit Interrupter or GFCI. It can either be equipped in your electric panel as a GFCI breaker, or in a GFCI outlet which also lets you extend the GFCI protection to other outlets "down the line" from the GFCI outlet.
If it's a GFCI receptacle and the button is not resetting then change the GFCI outlet.
Not if the GFCI breaker is supplying the circuit you are wanting to put the GFCI receptacle into.
Ground wire is loose or disconnected somewhere in that circuit.
Yes, but you can feed multiple outlets from one GFCI outlet. Make the first outlet fed in the cicuit a GFCI. Search for GFCI outlet with Google, etc. and I'm sure you will find an explanantion of how. Most GFCI's come with instructions also.
No, except that you insert the wires into the holes on the back of the outlet. The power in connects to the LINE side of the outlet and power out connects to the LOAD side of the outlet. This is clearly marked on the back of the outlet. This will not only protect the outlet with the GFCI installed but all outlets receiving their power from that GFCI. If you do not want to protect the outlets receiving power from the outlet then connect that outgoing wire to the LINE side also. But know that only the outlet with the GFCI will be protected and all other outlets will not be GFCI protected.
Yes you can. Lots of blow dryers have GFCI protection built in.
In a word NO, that will not cause either GFCI to trip. The correct term is GFCI (Ground Fault Circuit Interrupter)
I assume you are hard wiring it and not plugging it in. The power coming into the GFCI outlet connects to the line side of the GFCI outlet. If you want the outdoor timer protected by the GFCI then connect the wire going to the timer to the load side of the outlet. If you do not want the timer protected then connect it to the line side. On the back of the GFCI if you look closely you will see Line & Load marked on the back.
Click the link.
A down stream receptacle that is connected to the upstream GFCI will be protected. If the downstream receptacle senses a fault the upstream GFCI will trip.
A load of 1600 watts should be placed on a 20 amp 120 volt GFCI outlet.
GFCI Breakers are quite a bit more expensive than a GFCI outlet. More often than not a typical residence will need only a handful of GFCI outlets that combined together will be cheaper than a GFCI breaker. If you need to protect a series of outlets with GFCI protection you can simply connect the rest of the outlets on that same circuit downstream from the first outlet on the line and make that the GFCI. All you have to do is connect all the other outlets to the LOAD side of the GFCI outlet. If a GFCI fault occurs in any of the outlets down stream they will trip that very first GFCI plug you placed and keep you safe.