Can a 12-2 wire be connected to a 20-amp 240-volt circuit breaker to power a 240-volt heater?

There are limitations.

If there is a 120-volt fan in the heater, it will be necessary to run a 12-3 wire, so that there is a conductor for the 120 load neutral.

With a strictly 240 operation, the maximum wattage that can be served by a 20-amp circuit is 3840 watts. It is allowed to continuously operate a circuit at 80% of it's rated ampacity [4800 watts]. Continuous operation is defined as 4 hours or more continual operation.

<><><>

As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized.

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

No. The ampacity of a #12 wire is 20 amps. Being connected to a 30 amp breaker means that the wire can be overloaded by 10 amps and still not trip. There are two things that can be done to stay within the electrical code. Number one, change the two pole 30 amp breaker to a two pole 20 amp breaker. The load of the heater is I = W/E, 2000/240 = 8.3 amps. That load can be run on a 14-2 cable from a two pole 15 amp breaker. Remember that the breaker protects the size of the wire that is connected to it. Number two, if you want to use the 30 amp breaker then a #10 wire rated at 30 amps is the smallest wire to connect to that breaker.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

Yes

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you use 12-2 with ground to wire a 2000 watt forced air heater to a 240 volt 30 amp breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

What size breaker and wire for 2000 watt heater?

A 2000 watt heater draws 8.3 amps on a 240 v supply, so the cutout should be set to 10 or 12 amps. &lt;&lt;&gt;&gt; In North America a 2000 watt baseboard heater will be fed with a two pole 15 amp breaker. A two wire cable of #14 copper will be used to connect the supply voltage to the heater.


How can you plug 2000 watts 240v into a 120v 20 amp breaker with out replacing your breaker and all the plugs on the line?

You can't.


How many amps does a 2000 watt heater draw at 240 volts?

Amps * Volts = Watts So, Watts / Volts = Amps 2000 / 240 = 8.333 Amps You should run the circuit on a two pole 15 Amp breaker, using 14 AWG, 2 conductor (plus ground) wire, just so you have a little safety factor in the circuit size.


Can you use 240 volts for a 208 volt heater?

This is not recommended. The heater will operate at more than its given specified wattage. A 208 volt heater run off 220 volts will have an output increase by 11.87 percent. Similarly, a 220 volt heater can be run off of 208 but the wattage will be reduced by 10.61%. The calculations, using Ohms' Law, are shown below.Watts = volts x amps (W = V x I) and I = W / V so, if we take a 2000 watts heater designed to run on 208 volts, I = 2000 / 208 = 9.6 ampsResistance = volts / amps (R = V / I) so the heater's resistance is 208 / 9.6 = 21.632 ohmsAmps = volts / resistance (I = V / R) so, running on 220 volts, I = 220 / 21.632 = 10.17 ampsW = 220 x 10.17 = 2237 watts, which is an increase of 2237/2000 = 11.87%.W = V x I and I = W / V so, if we take a 2000 watts heater designed to run on 220 volts, I = 2000 / 220 = 9.09 ampsR = V / I so the heater's resistance is 220 / 9.09 = 24.2 ohmsI = V / R so, running on 208 volts, I = 208 / 24.2 = 8.595 ampsW = 208 x 8.595 = 1787.76 watts, which is a decrease of ( 2000-1787.76 ) / 2000 = 10.61%.


How many watts in 2000VA?

Up to 2000 watts. 2000 VA means the voltage times the current equals 2000, which must be multiplied by the power factor to find the power. The power factor depends on which type of load is being used. A heater has a power factor of 1, a motor around 0.8.

Related questions

What size breaker and wire for 2000 watt heater?

A 2000 watt heater draws 8.3 amps on a 240 v supply, so the cutout should be set to 10 or 12 amps. &lt;&lt;&gt;&gt; In North America a 2000 watt baseboard heater will be fed with a two pole 15 amp breaker. A two wire cable of #14 copper will be used to connect the supply voltage to the heater.


Does 2000 Acura TL Blower Motor Have A fuse?

I think it is called the heater motor and has a circuit breaker and a 40 amp fuse in the under hood fuse compartment.


How do you change a heater core on a 2000 Chevy impalla?

how do i change a heater core on a 2000 Chevy impalla


Heater sensor circuit Chevy Astro 2000?

heater sensor circuit Chevy astro 2000


How many btus in a 2000 watt heater?

2000


Can you replace a 2000 A Circuit breaker with 3150 A rating?

No.


How do you fix heater core in 2000 new beetle?

In order to probably repair the heater core in your 2000 New Beetle, you will probably have to get the entire heater core replaced.


How do you replace heater core in 2000 Pontiac grand prix?

where is the heater core at


How do you replace heater core in a 2000 Pontiac grand prix?

where is the heater core at


Why is your 2000 Ford F550 ruining so many heater cores?

Start with the electrical ground strap between the engine block and the battery and the Chassis. If either of these are even a tiny bit questionable it will cause electricity to go through the coolant and ground through the heater cor and radiator. This will cause corrosion and ruin the core.


How can you plug 2000 watts 240v into a 120v 20 amp breaker with out replacing your breaker and all the plugs on the line?

You can't.


Can you run a 2 kw convector heater through a 25 amp trip switch at 240 volts?

Yes, the total amperage load of a 2000 watt heater at 240 volts is 8.3 amps. Keep in mind that the wire feeding the heater must be a #10 because the breaker is rated at 25 amps. A wire's ampacity rating can be larger that the breaker amperage rating but never smaller. Example, a #14 rated at 15 amps or a #12 rated at 20 amps can not be connected to a 25 amp breaker. The 25 amp breaker does not trip until it reaches 25 amps well over the allowable amperage of the #14 amd #12 wire. This is why a #10 wire must be used as its rating is 30 amps.